It has been said every where I read that 3 phase does not save any money on the electric bill over single phase with the exception of motors.
Here is my situation. My plant has 3 rows of HID low bay lights on one 230v 2 pole 30 a breaker.
Each row draws 8 amps at 230v.
watts law for single phase: v x a x pf = watt's so 230 x 24 x .9 = 4968 watts or 4.9 kw
Now if I split the load into 3 balanced circuits on 3 phase: Watt's law for 3 phase: volts pr phase x amps pr phase x pf x 1.732 = watts.
so... 230 x 8 x .9 x 1.732 = 2868.1 watts or 2.8 kw.
So if we are billed in kwh it looks to me that 3 phase saves money. So where is the flaw in my logic? What am I missing here? :dunce:
Thanks in advance for any help!