• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

Wattstopper ELCU 200, Emergency Lights are very dim when Test Loop is open.

Status
Not open for further replies.

BJdittman

New User
Location
Maryland, USA
Occupation
Electrician
If anyone is knowledgeable about the Wattstopper ELCU 200 in conjunction with the LMRC 211 I have a question based on the current desires of the customer.

Modules Used:
ELCU - 200 (Emergency Control Unit)
LMRC - 211 (Control Panel)
LMSW - 101 (One Button Light Switch)
LMDC - 100 (Occ Sensor)
LMCT - 100 (Programmer)

Customer Wants: When the fire alarm system goes off for any reason they want the Emergency Lights in the building to go to 100% no matter what.

They are only providing one circuit for us for the ELCUs, is it possible to share the same circuit for emergency and normal power? We cut the test loop wire (Blue wire) and put it on an NC Relay circuit in the Fire Alarm System. Everything seems to work just fine but when the Fire Alarm goes off, or we disconnect the Test Loop the lights on the emergency only shine very dimly, making very little difference in a dark room. If you disconnect the dimming wires from the Emergency Lights during that state the lights shine at 100%.
Is there something in the programming? Something wired funny?


ELCU-200-Wiring-Diagram.png
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Did you also disconnect power to the LMRC?

The fixtures should go full-on when power is cut on the normal supply side.




Go to the supporting documents tab and read the emergency lighting bulletin.


Sent from my iPhone using Tapatalk
 

tank728

Senior Member
Location
New Jersey
Occupation
Electrician
Brantmacga hit the nail on the head. Constant power must be removed from the lmrc in order for the lights to go full bright. As you can see from your wiring diagram the elcu does not affect the dimming circuit (0-10). When power is lost to the lmrc it opens the dimming circuit, enabling the lights to go full bright
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Thinking over this again, you’re going to need a shunt relay. Because a fire alarm signal doesn’t equate to a power loss. So the only way to get full-on levels from the emergency lights is to disconnect normal power and the dimming circuit, and you’ll need a shunt relay to do that.

Here’s a Wattstopper part …





Sent from my iPhone using Tapatalk
 
Status
Not open for further replies.
Top