Wattstopper Powerpack/Sensor Wirinf

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
I have seen anything from 24 AWG to 16 AWG, it is often a 'what do we have laying around' decision.

The power packs control side is class 2 so any size is safe.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree with Bob, it's usually what's left over from some other application or what they have laying around in the shop. If I were ordering cable I would usually order #18 AWG stranded.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
The 2250 comes with an isolated relay. Is this a separate companent that needs installation. We have (4) of these sensors? THanks.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Sorry guys. Referencing the link above is the hot and neutral hitting the power pack then the light the lighting branch circuit or is it "above and beyong that" and must be included. Why I am saying that is because of the branch is already figured then more would not be needed. Only wiring from the sensor to the power pack. Thanks
 