A Alwayslearningelec Senior Member Location NJ Occupation Estimator May 6, 2020 #1 Any recept that's WP should be a GFI, correct? Drawing show a WP recept but don't call for it to be GFI.
Any recept that's WP should be a GFI, correct? Drawing show a WP recept but don't call for it to be GFI.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician May 6, 2020 #2 No, it may be that the location requires GFCI protection but that does not have to come from the receptacle itself it could be a WR listed receptacle and a GFCI circuit breaker or another upstream GFCI device providing the GFCI protection.