electricman2

Senior Member
Location
North Carolina
Occupation
Retired Electrical Contractor
Has anyone noticed 406.8(A) and (B) in the 2008? I went to the P&S site and found This article . Will all receptacles be weather resistant or will there be a different one for indoors? Sounds like another manufacturer driven change to sell more expensive receptacles.
 

frizbeedog

Senior Member
Location
Oregon
electricman2 said:
Has anyone noticed 406.8(A) and (B) in the 2008? I went to the P&S site and found This article . Will all receptacles be weather resistant or will there be a different one for indoors? Sounds like another manufacturer driven change to sell more expensive receptacles.

Does anyone know how these receptacles are constructed?

What's different that makes them wheather resistant over standard type?
 

frizbeedog

Senior Member
Location
Oregon
oops

oops

frizbeedog said:
Does anyone know how these receptacles are constructed?

What's different that makes them wheather resistant over standard type?

Nevermind, just saw it in the P&S link.

Any background as to how we got here.
 

iwire

Moderator
Staff member
Location
Massachusetts
frizbeedog said:
Any background as to how we got here.


Sure, here is some.

18-28 Log #3639 NEC-P18 Final Action: Accept in Principle
(406.8(A))
________________________________________________________________
Submitter:
Aaron B. Chase, Leviton Mfg. Co. Inc.

Recommendation: Revise text to read:
406.8 Receptacles in Damp or Wet Locations.
(A) Damp Locations. A receptacle installed outdoors in a location protected
from the weather or in other damp locations shall have an enclosure for the
receptacle that is weatherproof when the receptacle is covered (attachment plug
cap not inserted and receptacle covers closed).
An installation suitable for wet locations shall also be considered suitable for
damp locations.
A receptacle shall be considered to be in a location protected from the
weather where located under roofed open porches, canopies, marquees, and the
like, and will not be subjected to a beating rain or water runoff.
The receptacle shall be a Listed weather-resistant type.

Substantiation: The protection of outdoor receptacles in damp locations via
weatherproof cover plates is commendable. Unfortunately in reality, the outlets
intended to be protected are often subjected to exposure to water; UV and
impact. The protection of outlets typically used in indoor environments as well
is often not afforded this protection as anticipated by the current text of 406.8.
Unfortunately, many of these protective covers are defeated by either the user
intentionally or unintentionally breaking off the protective covers. Often in
other cases there is a misapplication of the proper cover plate when a vertical
closing plate is used in a horizontal application due to limited space after
construction was planned out. The submitter has also seen unfortunately in the
South Eastern USA a propensity for outlet covers not to be the self closing type. Additionally, 406.8 is misapplied in that the weatherproof enclosure is
often used with a product that 406.8(B)(2)(a) addresses as a product needing a
wet while-in-use cover. This often results from the homeowner’s needs.
Consequentially, receptacles are being exposed to moisture, UV and impact
under detrimental conditions (low temperatures). These products have not been
constructed or evaluated to being exposed to harsh conditions. An appropriately
Listed weather resistant outlet (able to withstand the harsh elements) is needed
to address the associated hazards with electrical products and outdoor use.
Statistical data* has illustrated the need for a more weather resilient device in
spite of the use of protective covers. The inclusion of the proposed additional
text in conjunction with the existing code language would address this
dangerous condition and noted failure rates.
*A joint NEMA/UL Field study revealed that the greatest number of
inoperable GFCI receptacles were located outdoors. The rate of failure was
more than double the next highest known location.

Panel Meeting Action: Accept in Principle
In addition to the recommended text, add a new last sentence to read as
follows:
This listed weather-resistant requirement shall become effective on January 1,
2011.

Panel Statement: A new last sentence was added to ensure availability.

Number Eligible to Vote: 12

Ballot Results: Affirmative: 12
________________________________________________________________
 

Chenley

Member
Location
Western KY
Kentucky will be going to the '08 on June 6th I believe. Haven't heard of anything not getting accepted. The local supply house is already getting stock of what will be needed for the change.
 

JohnJ0906

Senior Member
Location
Baltimore, MD
iwire said:
Panel Meeting Action: Accept in Principle
In addition to the recommended text, add a new last sentence to read as
follows:
This listed weather-resistant requirement shall become effective on January 1,
2011.

I just wanted to point out that the last sentence (effective date 1-1-11) was not included in the final version as published.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
This sounds like a bunch of crap to me. The GFCI receptacles outside my house have been there for 20+ years and are still working. They don't even have in-use style covers on them. IMO the only palatable way to make this work is to make all GFCI receptacles weather resistant.
 