Weatherhead for SER cable

Status
Not open for further replies.

ckelley3

Member
I am running an overhead feeder to a detached garage where it is not economically feasible to go underground (LOTS of pavement). Taking #4 SER from main house panel, through basement to rear of house, up side of the house (to a point at least 12' above the ground to meet O/H clearance requirements), then #6 quadruplex to the garage. AHJ does not require conduit for service cables in this area, so SER will simply be attached to siding. I am trying to decide if there is any better form of protection for the end of the SER cable than the minimum "gooseneck" req'd by code. Most service entrances in the area use the plastic hoods, but the clamps on them are made for SEU, not SER. Friend of mine who works as an estimator for large contractor said his company always uses a metal weatherhead (made for RMC) clamped to the SER, as the AHJ likes to see something other than a gooseneck. Opinions?
 
Using an RMC weatherhead for SER cable is no good unless it's also listed for SER cable terminations. No one makes an SER weatherhead? Although a gooseneck is ugly it is permitted by the NEC.
 
I have searched high and low for an SER weatherhead. Chief inspector from AHJ doesn't know of one either. I check with the mfr of the SEU weatherhead and it is NOT listed for SER cable. Looks like I'm gonna have to use pipe or gooseneck it.
 
Maybe sleeve short section at top with a piece of PVC and cap with PVC weatherhead?

Would solve the issue of needing to ground the weatherhead, may look strange but might look better than a gooseneck, then again it might not. Either way looks kind of hacked. I would run this in a raceway myself - even if proper head was available - but that is just me.
 
Status
Not open for further replies.
Top