qcroanoke
Sometimes I don't know if I'm the boxer or the bag
- Location
- Roanoke, VA.
- Occupation
- Sorta retired........
When are the in use receptacle covers required?
Our 3rd party inspection agency is telling us we
MUST always use an "In use" receptacle on an outdoor receptacle.
I exclude us from needing this cover by quoting
section 406.8(B)(2)(b)Which to me says if you have an outdoor receptacle that is used only while attended the cover need not be The "In use"type.
He is using the explanation of that section which says the section only applies to other than 15 or 20 amp 125 and 250 volt receptacles.But the code section itself does not say that.
I think the explanation is wrong.
If I'm wrong so be it.
Can someone give me an explanation or interpertation of this section?
Do we have to always use "in use" covers no matter what? And,if so why are the other covers even available?
All responses will be appreciated!
Our 3rd party inspection agency is telling us we
MUST always use an "In use" receptacle on an outdoor receptacle.
I exclude us from needing this cover by quoting
section 406.8(B)(2)(b)Which to me says if you have an outdoor receptacle that is used only while attended the cover need not be The "In use"type.
He is using the explanation of that section which says the section only applies to other than 15 or 20 amp 125 and 250 volt receptacles.But the code section itself does not say that.
I think the explanation is wrong.
If I'm wrong so be it.
Can someone give me an explanation or interpertation of this section?
Do we have to always use "in use" covers no matter what? And,if so why are the other covers even available?
All responses will be appreciated!