flashlight
Senior Member
- Location
- NY, NY
- Occupation
- Electrician, semi-retired
A 200A fused disconnect switch with 150A fuses is fed by 1/0 service conductors. On the load side are duplex lugs.
Can the tap rules of 240.21 be applied to conductors fed from these duplex lugs ?
E.g. #8 s can run less than 3m in conduit to a subpanel where they
are protected by a 40A breaker ?
Can the tap rules of 240.21 be applied to conductors fed from these duplex lugs ?
E.g. #8 s can run less than 3m in conduit to a subpanel where they
are protected by a 40A breaker ?