Weigh belt in Class II, Div 2 location

Status
Not open for further replies.

joshtrevino

Member
Location
Beaumont, TX
I am installing a weigh belt in a Class II, Div 2 Group F location. Does the NEC require that the load cells on the weigh belt be intrinsically safe? Other requirements?
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Division 2 (any Class) rarely needs intrinsically safe or nonincendive wiring methods, they're OK of course, just not necessary unless the load cells are not suitable for the classification. Check Section 502.10 for other appropriate wiring methods,
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I can't imagine load cells that would not be suitable for a Class II location. I would be concerned about static discharge, and other electrical equipment on the weigh belt if the weigh belt was not designed to handle combustible dusts.
 
Status
Not open for further replies.
Top