Just thought id throw this out here to see if anyone has a less crackpot theory about what is going on here than me
So a bit of history and a description of the system; I'm providing electrical tech support and maintenance to a company that operates ROVs in the Pacific ocean. The system uses 5 vfds on the boat to drive the ROV under the water. All 5 thruster circuits run in a 20C tether between the boat and the rov and split into 5 separate cables at either end of the tether. The OEM machine came with a fancy all in one cable with each motor having a braided shield around the individual motor conductors. Due to the challenges of covid I've had to source out an American made alternative and I've done away with the braid because of vibration caused by a high-pressure water hose running parallel to our tether cause the cables to wear out from the friction of the braids in about 4 months. They have been working great for over a year now requiring rebuilds more or less just from operator "wear n tear". 400v system, 2.5hp motors, #16 wire, 100m tether, Flygt SR 4620 motors. Cable connects to thruster with a subsea connector resembling a pin/sleeve connector.
So anyways, I've had 2 cables recently fail in a weird way. When doing loop checks and insulation tests the cable passes perfectly. Plug it into a motor and fails at about 300kohms. It'll fail when plugged into any other Flyght 4620 motor. Cut the subsea end off and twist the power conductors together to simulate motor windings...pass on the insulation test, install new subsea connector and fail again.
So I replace the cable and everything is happy again. I leave the cable sitting at the shop for a couple months and it seems ok now but i haven't tried putting it back into service yet. Ill be running it for a few hours with a spare unit in a tank at the shop in a week or two. A week ago I go out to another boat, same issue with a different cable/core numbers inside the cable, troubleshoot it the systematically in the same way. I cant repair it at the location the boat is at so we make a plan for a week later. Operators run the machine and over the course of the weekend the cable takes out the thruster motor, motor is extremely hot when it comes out of the ocean. The motor ran for 2 straight days and i can only speculate that the short circuit current wasn't too high because the vfd is limited in the settings at 5.7A. I replaced the cable and thruster a couple days ago and the cable is on my bench to disassemble and troubleshoot. It appears to be a problem "with" the tether that "affects" the motor and not the tether.
Curious if anyone has seen something like this before and can shine some light on what could be going on or how to test for it? Best theory i can come up with is one of the cores is magnetized somehow which moves a some internal component in the motor? Or that some other quality of the wire insulation other than resistance has been degraded? I'm out of my depth a bit with this one.
So a bit of history and a description of the system; I'm providing electrical tech support and maintenance to a company that operates ROVs in the Pacific ocean. The system uses 5 vfds on the boat to drive the ROV under the water. All 5 thruster circuits run in a 20C tether between the boat and the rov and split into 5 separate cables at either end of the tether. The OEM machine came with a fancy all in one cable with each motor having a braided shield around the individual motor conductors. Due to the challenges of covid I've had to source out an American made alternative and I've done away with the braid because of vibration caused by a high-pressure water hose running parallel to our tether cause the cables to wear out from the friction of the braids in about 4 months. They have been working great for over a year now requiring rebuilds more or less just from operator "wear n tear". 400v system, 2.5hp motors, #16 wire, 100m tether, Flygt SR 4620 motors. Cable connects to thruster with a subsea connector resembling a pin/sleeve connector.
So anyways, I've had 2 cables recently fail in a weird way. When doing loop checks and insulation tests the cable passes perfectly. Plug it into a motor and fails at about 300kohms. It'll fail when plugged into any other Flyght 4620 motor. Cut the subsea end off and twist the power conductors together to simulate motor windings...pass on the insulation test, install new subsea connector and fail again.
So I replace the cable and everything is happy again. I leave the cable sitting at the shop for a couple months and it seems ok now but i haven't tried putting it back into service yet. Ill be running it for a few hours with a spare unit in a tank at the shop in a week or two. A week ago I go out to another boat, same issue with a different cable/core numbers inside the cable, troubleshoot it the systematically in the same way. I cant repair it at the location the boat is at so we make a plan for a week later. Operators run the machine and over the course of the weekend the cable takes out the thruster motor, motor is extremely hot when it comes out of the ocean. The motor ran for 2 straight days and i can only speculate that the short circuit current wasn't too high because the vfd is limited in the settings at 5.7A. I replaced the cable and thruster a couple days ago and the cable is on my bench to disassemble and troubleshoot. It appears to be a problem "with" the tether that "affects" the motor and not the tether.
Curious if anyone has seen something like this before and can shine some light on what could be going on or how to test for it? Best theory i can come up with is one of the cores is magnetized somehow which moves a some internal component in the motor? Or that some other quality of the wire insulation other than resistance has been degraded? I'm out of my depth a bit with this one.