Fred B
Senior Member
- Location
- Upstate, NY
- Occupation
- Electrician
So had a service call the other day that overnight lost power on portion of circuit. (Did have storms overnight.) Customer states they had tried to use the shredder in the morning and nothing, assumed the shredder was shot but decided to try a different receptacle, and it worked. He then stated he knew the receptacle had some damage so he decided to replace it. He did the replacement and then the TV on same line stopped working. That is when he called me. First thing was to check the receptacle that he replaced to see if it was wired correctly, connection in correct place. But when I metered first with the circuit tester it showed hot/groung reversed. Put on the volt meter checked Hot-neutral, 6V; hot-ground, 0V; gound-neutral, 116V. Started tracking back toward the origin of circuit next receptacle also showed hot-ground reversed, etc until I got to a good reading. Now he hadn't per his statement changed any other receptacle. Started to open up to see if it had a wire disconnect and make a short that wasn't tripping breaker. Found none, all were wire correctly. Ground-hot did show continuity from the load side at the 4th receptacle but not on line side, so I've isolated the area. Working my way back checking each receptacle for the shorted connection an found none, it did have a gas fireplace that used a connection in between the tested points. Assuming this load had gotten damaged in the storm disconnected it (plug-in unit). Reconnected the everything except the fireplace. Turned on power and retested. All receptacles tested ok, no reversals. Plugged in the power strip for the TV and suddenly got a reversal on the lines again. Unplug the power strip, and still have the reversal. Now really puzzled. Shut off power and re-metered, everything metered correctly between receptacles. So thought could it be power strip, so just plugged in the TV and the cable box (the loads on that circuit) Turned on power and no further reversal. Plugged additional load on line and it still held. So it seems to be related to the power strip.
But the question that puzzling is why did the tester still read as a reversal when I removed the power strip until I turned off breaker and then turn it back on? But if the condition is load related, as that seems to be a more logical situation given the reversal remains until breaker is turned of then reset, does it only present when the loads are applied via the power strip?
But the question that puzzling is why did the tester still read as a reversal when I removed the power strip until I turned off breaker and then turn it back on? But if the condition is load related, as that seems to be a more logical situation given the reversal remains until breaker is turned of then reset, does it only present when the loads are applied via the power strip?