hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have 480V three phase coil line that has three phase motor. That’s the only load
The incoming service from panelboard is 208/120V three phase
So they placed a regular dry type distribution with primary voltage of 480V delta terminals H1,H2,H3 to secondary 240/120V wye terminals X1,X2,X3,X0 dry type transformer.
Only thing is the transformer is wired reversed so primary now is 208V and no neutral is brought to the X0 terminal. So I have three phase conductors and EGC brought.
The secondary now is 480V of course has no neutral terminal it’s H1, H2, H3 and has EGC but not the same size as the primary.
Questions:
1. Would the above be Separately derived system (SDS) or non separately derived system (NSDS)? Only load I have is three phase motor secondary.
2. How can one go about grounding if it is SDS no neutral is brought and which side 208V or 480V should be grounded?
3. Does the secondary 480V side require breaker protection and what about secondary cable size for the transformer?
4. Manufacturer datasheet says primary 480V delta and secondary 208/120V. By using it in reverse it’s not in compliance with NEC 2014 Section 110.3(B)? Any thoughts opinions
The incoming service from panelboard is 208/120V three phase
So they placed a regular dry type distribution with primary voltage of 480V delta terminals H1,H2,H3 to secondary 240/120V wye terminals X1,X2,X3,X0 dry type transformer.
Only thing is the transformer is wired reversed so primary now is 208V and no neutral is brought to the X0 terminal. So I have three phase conductors and EGC brought.
The secondary now is 480V of course has no neutral terminal it’s H1, H2, H3 and has EGC but not the same size as the primary.
Questions:
1. Would the above be Separately derived system (SDS) or non separately derived system (NSDS)? Only load I have is three phase motor secondary.
2. How can one go about grounding if it is SDS no neutral is brought and which side 208V or 480V should be grounded?
3. Does the secondary 480V side require breaker protection and what about secondary cable size for the transformer?
4. Manufacturer datasheet says primary 480V delta and secondary 208/120V. By using it in reverse it’s not in compliance with NEC 2014 Section 110.3(B)? Any thoughts opinions