Hello,
I have somewhat of a weird scenario, I'm hoping someone can shed some light on my issue.
I am on a job where I only have 1 EM circuit, 277VAC. It is shared between multiple floors.
In my unit I have installed lights for both 277VAC EM lighting, and 120VAC EM lighting. I have nLight lighting controls for my lights.
My lights on the 277VAC EM are fine, controls work, et cetera. This is feeding straight from the breaker, on another floor.
Since this is my only EM circuit and I have 120VAC EM lights, I have to step-down the voltage, obviously with a step-down transformer.
I have now gone through 3 different step-down transformers, all resulting with the same issues.
1) I hook up L1 on H1, L2 on H2 (277VAC)
2) X1,X3 together, X2,X4 together, no other leads coming off the step-down to hook-up
3) testing voltage off the leads gives me hot on X1,X3, neutral on X2,X4
4) test voltage, 120VAC
So, I have what I need right off the leads. From my leads I have a 12/2 MC carrying the 120VAC to a J-Box. With nothing connected to my 12/2 whip in the J-Box, both hot and neutral carry voltage. 120VAC between hot and neutral, 12VAC to ground on hot and neutral.
My loads I need to connect to this are:
1) 120VAC EM lights, being feed through an nLight EM power-pack (this power-pack works, I have temped in from another local 120VAC power source to verify devices are working correctly, they are when not connected to the secondary of the step-down)
2) 120VAC fire-dampers
When I hook-up the fire-dampers, only, I get 60VAC on both neutral and hot.
When I hook-up the power-pack, only, I get back feed only the neutral, 120VAC.
When I hook-up both loads, I get voltage only on the neutral.
I have set the transformer up in every configuration, I still get the same issue.
Whether I go parallel, X1-X3, X2-X4; series and pull neutral off X2-X3; or even isolate coils; I still get the same weird voltages.
At this point I'm wondering if a bonding jumper would help to create a new neutral, or maybe the service has an issue with their neutral installation; but I'm not sure if I would want to bond that on the load side. Anyway, my guess is there is something up with the system neutral, any help is greatly appreciated! Thank you!
I have somewhat of a weird scenario, I'm hoping someone can shed some light on my issue.
I am on a job where I only have 1 EM circuit, 277VAC. It is shared between multiple floors.
In my unit I have installed lights for both 277VAC EM lighting, and 120VAC EM lighting. I have nLight lighting controls for my lights.
My lights on the 277VAC EM are fine, controls work, et cetera. This is feeding straight from the breaker, on another floor.
Since this is my only EM circuit and I have 120VAC EM lights, I have to step-down the voltage, obviously with a step-down transformer.
I have now gone through 3 different step-down transformers, all resulting with the same issues.
1) I hook up L1 on H1, L2 on H2 (277VAC)
2) X1,X3 together, X2,X4 together, no other leads coming off the step-down to hook-up
3) testing voltage off the leads gives me hot on X1,X3, neutral on X2,X4
4) test voltage, 120VAC
So, I have what I need right off the leads. From my leads I have a 12/2 MC carrying the 120VAC to a J-Box. With nothing connected to my 12/2 whip in the J-Box, both hot and neutral carry voltage. 120VAC between hot and neutral, 12VAC to ground on hot and neutral.
My loads I need to connect to this are:
1) 120VAC EM lights, being feed through an nLight EM power-pack (this power-pack works, I have temped in from another local 120VAC power source to verify devices are working correctly, they are when not connected to the secondary of the step-down)
2) 120VAC fire-dampers
When I hook-up the fire-dampers, only, I get 60VAC on both neutral and hot.
When I hook-up the power-pack, only, I get back feed only the neutral, 120VAC.
When I hook-up both loads, I get voltage only on the neutral.
I have set the transformer up in every configuration, I still get the same issue.
Whether I go parallel, X1-X3, X2-X4; series and pull neutral off X2-X3; or even isolate coils; I still get the same weird voltages.
At this point I'm wondering if a bonding jumper would help to create a new neutral, or maybe the service has an issue with their neutral installation; but I'm not sure if I would want to bond that on the load side. Anyway, my guess is there is something up with the system neutral, any help is greatly appreciated! Thank you!