Twoskinsoneman
Senior Member
- Location
- West Virginia, USA NEC: 2020
- Occupation
- Facility Senior Electrician
Installing a single receptacle installed on an individual branch circuit exclusively for the use of a cord and-plug-connected arc welder. The manufacturer recommends a 20A recep with a 30A ocpd. The welder nameplate lists I1max 21.4A and I1eff 11A. 210.21(B) and 630.11 seem to allow the manufacturers recommendation.
Is this ok? I would think that the next guy that owns this house may not have a welder and this will end up being a general use 20a recept on a 30a ocpd.
Is this ok? I would think that the next guy that owns this house may not have a welder and this will end up being a general use 20a recept on a 30a ocpd.