OK.....Here is my stumper for today....
The maximun overcurrent protection device rating for a #10THHN used for an arc welder branch circuit is...
A. 30a
B. 40a
C. 50a
D. 70a
My thinking is it is 80a based on 630.12 (B). #10 THHN is rated at 40a from 310.16 and I just went to 200% of that. But 80a is not a choice so I guess I'd go for answer D. Any takers?