Fellas,
630.12 Overcurrent Protection..........................."Where the values as determined by this section do not correspond with the standard ampere ratings provided in 240.6 or the rating or setting specified results in unnecessary opening of the overcurrent device, the next higher standard rating or setting shall be permitted."
630.12(B) For Conductors. Conductors that supply one or more welders shall be protected by an overcurrent device rated or set at not more than 200% of the conductor ampacity.
My question, what if the next "standard size" exceeds 200%? This question came up in class last night and I could not answer it.
Thanks guys,
Steve
630.12 Overcurrent Protection..........................."Where the values as determined by this section do not correspond with the standard ampere ratings provided in 240.6 or the rating or setting specified results in unnecessary opening of the overcurrent device, the next higher standard rating or setting shall be permitted."