Another C10
Electrical Contractor 1987 - present
- Location
- Southern Cal
- Occupation
- Electrician NEC 2020
Just curious if I read this nameplate correctly.
and would you do what is technically correct or what is realistically fine.
I was going to provide some #6 for this 240v 1 ph welder which is about 30 ft from the panel source and
they like to use 100' cords to make their welders more portable.
I figured ( A ) is intermittent ( 60 % ) and steady ( 100% )
( B ) being the amperage of 51A , 60% / 36A, 100%
They have several welders already, I'm providing 3 more welder receptacles (each independent 240 1 phase circuits )
The existing welders all use 50 A Receptacles throughout the shop.
I was just contemplating, do I go with matching their original design based on this existing equipment
or do I get all technical based on the nameplate and have 1 receptacle 60 A rated, therefor no other welders
can use the new receptacles I install, based on the existing cord end configuration.
My questions to you guys is .. would you match the existing design knowing that they are slightly under the welder capability
or do you do what I'd rather do and rate the new receptacles to accommodate the 50 + amp ability.
I'm probably going to just keep the new receptacles at the 50 A rating and hope the additional 1-3 amps wont do much overheating at the plug

and would you do what is technically correct or what is realistically fine.
I was going to provide some #6 for this 240v 1 ph welder which is about 30 ft from the panel source and
they like to use 100' cords to make their welders more portable.
I figured ( A ) is intermittent ( 60 % ) and steady ( 100% )
( B ) being the amperage of 51A , 60% / 36A, 100%
They have several welders already, I'm providing 3 more welder receptacles (each independent 240 1 phase circuits )
The existing welders all use 50 A Receptacles throughout the shop.
I was just contemplating, do I go with matching their original design based on this existing equipment
or do I get all technical based on the nameplate and have 1 receptacle 60 A rated, therefor no other welders
can use the new receptacles I install, based on the existing cord end configuration.
My questions to you guys is .. would you match the existing design knowing that they are slightly under the welder capability
or do you do what I'd rather do and rate the new receptacles to accommodate the 50 + amp ability.
I'm probably going to just keep the new receptacles at the 50 A rating and hope the additional 1-3 amps wont do much overheating at the plug