Welder single phase 240

Status
Not open for further replies.

Meisenburg

Member
Location
New York
Hey guys, I have Lincoln welder that says it's draws 68 amps at 240. Should I use 70 amp breaker? Also how do I properly size a welder like this thanks for your helps guys...
 

cpinetree

Senior Member
Location
SW Florida
Review NEC article 630

630.11
You will need to size the conductors for 68 amps.

630.12
The breaker can not exceed 200% of the 68 amps.
A 125amp breaker will most likely be fine.
 