Trying to install properly a 480V 3 phase Welder with a nameplate amp rating of 25amps.
To determine the conductor ampacity I look at the duty cycle which is 70 and it is a non motor generator so I believe I should multiply my 25amps by .84. This gives me 21 amps. I would then size my conductors conservatively at 30 amps or #10 wire. 630.11(a)
To size my breaker for one welder. I would use my amp rating of 25amps and multiply it by 200%. This would give me a 50 amp 3 phase breaker.
Am I on the right track here? What am I missing?