Looking for some back up on OCP & conductor calculations for a welder. Working on renovations to a welding lab. The new welders cut sheet shows the MIG welder @ 460V is 17.1A 60% Duty Cycle. Highlighted by me on page 4 of the cut sheet attached with this post
I will not get the I1eff for the welder & this is a non motor generated welder. So…..
Overcurrent
17.1 x 200% = 34.2A - 35A is OCP size.
Conductor
17.1 x .78 = 13.338A…..#12 (20A) I am using 75deg. column since C/B/disconnect and receptacle will all be rated for 75deg. Although with #12 this does not matter.
This also works with 630.12 (B) #12’s rated for 20A x 200% max = 40A Max C/B size permitted. Per above we are @ 35A.
Design question
The shop currently has a 277/480V switchboard with 60A C/B’s feeding existing welders. I would like to reuse these C/B’s to feed the disconnect switch (required per 630.13) with 40A time delay fuses in the disconnect switch. This disconnect switch would feed the welding receptacle.
Any thoughts on this design consideration?
Thanks for the replies
I will not get the I1eff for the welder & this is a non motor generated welder. So…..
Overcurrent
17.1 x 200% = 34.2A - 35A is OCP size.
Conductor
17.1 x .78 = 13.338A…..#12 (20A) I am using 75deg. column since C/B/disconnect and receptacle will all be rated for 75deg. Although with #12 this does not matter.
This also works with 630.12 (B) #12’s rated for 20A x 200% max = 40A Max C/B size permitted. Per above we are @ 35A.
Design question
The shop currently has a 277/480V switchboard with 60A C/B’s feeding existing welders. I would like to reuse these C/B’s to feed the disconnect switch (required per 630.13) with 40A time delay fuses in the disconnect switch. This disconnect switch would feed the welding receptacle.
Any thoughts on this design consideration?
Thanks for the replies