They are considered free-air, that is why you can use table 310.17. You can use the 90 degree column for de-rating purposes (temperature), but it cannot be higher than the 75 degree column because or the 75 degree limitations of the equipment you are connecting it to.Originally posted by mgb:
Even though they're single conductors and aren't in a conduit? Wouldn't they be considered "free air"?
I have a 1973 MGB.Originally posted by dereckbc:
Curious, your login name is MGB, is that your intials, or are you in the telecom sector?
Actually they are single conductors, I shouldn't have called them cables, sorry. But I'll probably go with RHH/RHW like dereckbc suggested. Thanks again, appreciate all the informative feedback!Originally posted by don_resqcapt19:
Steve,
I don't see how that exception would permit the use of welding cable. The exception only permits the use of single conductors as opposed to the cable or cord assemblies required in 527.4(B). It also does not modify 527.2(A).
Don