In two recents installations, a subcontractor used welding cable in separate capacitor bank projects due to the flexibility of the cable. For the 200kVAr bank he choose to go with 4/0 for the 3Ph Delta, on a 400 amp breaker. We are getting some increased temperatures in the wiring and conduit as a result. All seemed to be sized close enough to where it should not be heating up warm to the touch (excessively warm). It appears the wire is acceptable for the feeders but not the overcurrent protection (which doesnt explain the heat. Either way, does welding cable present an issue when used in this application? Does it typically heat up more so than THHN? I appreciate any help understanding your experiences. Thank you.