This is a two part question I am seeking input on;
Part I
I am looking for some input regarding 2008 NEC Article 630.41 & 630.42. The intension is to install a new 277/480V 400A panel to feed 8 welder receptacles using cable tray to install the MC Cable branch circuits for the receptacles. Plans were submitted and reviewed by a third party plan reviewer which is a requirement in order to receive an electrical permit. I did not prepare the drawings which were submitted however our client has come to us regarding the comments the reviewer made on the drawings one of which is requiring they be signed and sealed by a PE. The very first item he cited was;
Cable tray shall provide support at intervals not greater than 6? 630.42(a) A permanent sign shall be attached to cable tray every 20?. Sign shall read ?Cable tray for welding cables only? 630.42 (c)
I am questioning what the NEC is referring to where it says Welding Cable, Article 630 Part IV. We all know what the industry refers to as welding cable. However as far as the NEC is concerned there is no definition (at least none that I could find) for welding cable so, does this mean any type of cable (conductor) feeding a welder? Although in this case I am not feeding a welder I am feeding a receptacle which is used to plug a welder into. Seems odd why these conductors would be treated any differently than any other branch circuit conductor.:?
Part II
NEC Article 392 says if using single conductors in cable tray the minimum size it must be is 1/0 unless it is an EGC than minimum size is #4. What if I use a multi-conductor cable? There is no minimum size listed for this only that they are permitted to be installed in the cable tray 392.6 E. Is there a minimum cable size requirement?
Part I
I am looking for some input regarding 2008 NEC Article 630.41 & 630.42. The intension is to install a new 277/480V 400A panel to feed 8 welder receptacles using cable tray to install the MC Cable branch circuits for the receptacles. Plans were submitted and reviewed by a third party plan reviewer which is a requirement in order to receive an electrical permit. I did not prepare the drawings which were submitted however our client has come to us regarding the comments the reviewer made on the drawings one of which is requiring they be signed and sealed by a PE. The very first item he cited was;
Cable tray shall provide support at intervals not greater than 6? 630.42(a) A permanent sign shall be attached to cable tray every 20?. Sign shall read ?Cable tray for welding cables only? 630.42 (c)
I am questioning what the NEC is referring to where it says Welding Cable, Article 630 Part IV. We all know what the industry refers to as welding cable. However as far as the NEC is concerned there is no definition (at least none that I could find) for welding cable so, does this mean any type of cable (conductor) feeding a welder? Although in this case I am not feeding a welder I am feeding a receptacle which is used to plug a welder into. Seems odd why these conductors would be treated any differently than any other branch circuit conductor.:?
Part II
NEC Article 392 says if using single conductors in cable tray the minimum size it must be is 1/0 unless it is an EGC than minimum size is #4. What if I use a multi-conductor cable? There is no minimum size listed for this only that they are permitted to be installed in the cable tray 392.6 E. Is there a minimum cable size requirement?