1/0 flex-a-prene -50C to +105C heavy duty welding cable
-vs-
1/0 THWN/THHN 90C
75' feeder to 225A 3ph panel
1/0 welding cable (according to manufacture) is good for 250A
1/0 THWN/THHN (according to Table 310.16) is good for 170 A
1/0 THWN/THHN would require parallel, welding cable would not.
Welding cable is much easier to manipulate than thwn/thhn, esp
with the larger gauges.
I guess my question is, is it a prohibited procedure to utilize welding cable in lieu of THWN/THHN as a feeder?