welding cable

Status
Not open for further replies.

patriot

Member
Location
Chapmansboro,Tn.
Is it legal to use welding cable for feeders? I cant find anything in the code that says you cant. The only reason I can see that you can't use it is that the feeder is under ground and the welding cable is rated for 90C. It was suggested that I use it for a 500kw genarator install. I've used it on soft starts and vfd's but i've never used it underground.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
"welding cable" as such is not a 310.13 or 400.4 recognized conductor.
If it has an additional recognized insulation just as RHW, or type W then it may be used.
Note it is likely fine strand and will need special listed termination fittings.
 