Hey man,
Have a problem and need some advice.
Working in a school, installing some new distribution panels. Panel #1 800amp feeds several other small panels. Panel #2 also fed from #1 and is also a 800amp panel but plans call for a 450amp breaker and parallel 4/0 between the panels.
When I installed guts for panel #1 the breaker to feed panel #2 turned out to be a 800amp breaker so I ordered a 450amp breaker plug to replace the 800amp plug.
Ok here is where things go south, panel #2 is to feed 12 welding booths and buy my calculations has max load of 540amps(of course you would never run all welders at same time). The engineer that designed this (who is also the inspection authority in this case) is saying that he does not want the 450amp breaker plug installed and buy NEC code you are allowed to de-rate panel feed wires buy 200%. I cannot find this code allowance and very concerned that this is a potential disaster. As far as I can find panel to panel feed wire sizes are simply calculated based on the size of breaker feeding them. All the rest of panel feeds in building are correct as are every panel I have ever installed.
Are you aware of any code that would allow this engineer to get away with this?
Have a problem and need some advice.
Working in a school, installing some new distribution panels. Panel #1 800amp feeds several other small panels. Panel #2 also fed from #1 and is also a 800amp panel but plans call for a 450amp breaker and parallel 4/0 between the panels.
When I installed guts for panel #1 the breaker to feed panel #2 turned out to be a 800amp breaker so I ordered a 450amp breaker plug to replace the 800amp plug.
Ok here is where things go south, panel #2 is to feed 12 welding booths and buy my calculations has max load of 540amps(of course you would never run all welders at same time). The engineer that designed this (who is also the inspection authority in this case) is saying that he does not want the 450amp breaker plug installed and buy NEC code you are allowed to de-rate panel feed wires buy 200%. I cannot find this code allowance and very concerned that this is a potential disaster. As far as I can find panel to panel feed wire sizes are simply calculated based on the size of breaker feeding them. All the rest of panel feeds in building are correct as are every panel I have ever installed.
Are you aware of any code that would allow this engineer to get away with this?