I have installation issues needing code advice, suggestion or perhaps provide location in the code that may permit this application.
Multiple 1PH and 3PH receptacles set up for mig / tig welding machines and a few plasma cutters.
60A fused disconnect w/ 50A fuses wired to (2) 1PH 30A receptacle #10awg, and (1) 50A 3PH #8awg x 10’ SO cable receptacle plug.
I believe is safest approach 630.13 a single fused disconnect for each plug/welding machine, (only one of the machines has an integral disconnect)
Looking at 630.11 (B) unit duty cycle for group Arc welders may not apply as none are Arc welders, or do these machines apply.
The receptacle supply from 112.5kva 480X240 3 PH DELTA to 225A 3PH load center. Disconnect wired #8awg X200’ voltage reading L-L=V, L-G=0
Should the transformer be corner grounded? Or install ground detection system 250.21
Thank you