That's what I thought, until I read the following in the ANSI Z49.1 standard:
11.3 Installation of Arc Welding Equipment
11.3.1 Code Requirements. Installation including
grounding, necessary disconnects, fuses, and type of
incoming power lines shall be in accordance with the
requirements of the current NFPA 70, National Electrical
Code®, and all local codes.
11.3.2 The Work. The workpiece or metal upon
which the welder welds shall be grounded independent of
the welding leads to a good electrical ground unless a
qualified person assures it is safe to work on an
ungrounded workpiece.
E11.3.2 When the work terminal is grounded, care
should be taken to see that the workpiece is not separately
grounded. Refer to 11.3.2.1. Before welding is attempted
the operator should check to be sure that the worklead is
properly connected. This will eliminate the chance of
welding current being misdirected into the grounding
conductor system of other equipment. Misdirected
welding current can damage conductors which do not
have adequate ampacity. See Article 630.15 of NFPA 70,
National Electrical Code®.
11.3.2.1 Grounding. Grounding shall be done by
locating the work on a grounded metal floor or platen, or
by connection to a grounded building frame or other
satisfactory ground. Care shall be taken to avoid the flow
of welding current through a connection intended only
for safety grounding since the welding current may be of
a higher magnitude than the grounding conductor can
safely carry.
11.3.2.2 Work Lead. Welding current shall be
returned to the welding machine by cable with sufficient
current capacity. However, connection of a cable from
the welding machine to a common conductor or properly
bonded structure on which the work rests, or to which the
work is connected, shall be a permissible alternate
procedure. Single-phase alternating current machines in
groups of three with their inputs connected in delta to a
three-phase supply circuit connected in wye on the
secondary circuits shall be permitted to use a single work
lead from the neutral of the three units to the structure
being welded.
The work lead shall use a single cable of a size suitable
for the current rating of at least one machine.
This appears to me to require the work table to be grounded, separately from whatever work lead(s) may be clamped to the table.
Does anyone out there agree?