article 250.50 states all grounding electrodes described in 250.52 (a) (1) through (a) (6) that are present ateach bldg shall be used to form the grounding system. if not available than one or more of the electrodes specified in 250 52 (a) (4) through (a) (8) shall be used . my ques. is a bldg. 400 by 400 is being built for manuf and storage in this case 250 52 (a) (3) is present at the site . the service is 1600 amp 3 phase 208/ 120 .is grounding to the rebar which is longer than 30 feet and incased in concrete with a nunber 4 bare copper wire the only requirment to satisify the code requirment. 2nd ques there will be no water line going to the bldg but 75 feet away there ia a well which services other bldgs the casing for the well is steel and goes down at least 100 ft .this to me is a lot better grounding means then that piece of rebar.and should be used.if they were to use the well would they have to use 3/0wire and cad weld it to the well casing.as the service is 1600 amps. yet you only need a number 4 to the rebar