Well casing bonding pex piping.

Status
Not open for further replies.

AC\DC

Senior Member
Location
Florence,Oregon,Lane
Occupation
EC
So I am not using the casing as a GEC. Though the casing needs to be bonded to the EGC.
it would be easy enough to bond it but is it my responsibility?
The well installer is hocking up to the wire I ran. I will get inspection prior to well installer finishing job.
since he hocking up the system it’s his responsibility to tie into the EGC correct!
Correct?
 
ya after righting the op I thought that it’s a AHJ call.
This well driller is the same one I turned in about a year ago for doing illegal electrical work. So I trying to see how far he takes his work.
 
With a metal water piping system from the resdience to the well youi would bond the well casing to that pipe but there is no reuirement to bond the casinmg in general. As mentioned, with a submersible pump youi are required to biond the EGC to the casing.
 