I installed a 200 amp service at a new build.
I've got 2 ground rods 6' apart and have come from the main service with a #4 Cu conductor to the rods.( I realize this could be #6 but had 4 on the truck)
The Service load center is located in the garage. I've got a 100 amp sub feed to the basement .
At the time I installed the service there were no other grounding electrodes present. I was told that the well at the opposite end of the house was going to be entering the dwelling in plastic pipe.
Now I get back 3 months later and the well comes into the house in copper pipe.
Does code require that I now make the well casing connected by copper pipe part of the GEC ?
Or can I just bond the pipe to the EGC in the sub panel?
Getting a GEC back to the Service in the garage would be difficult at best.
Thanks