New construction, with well about 30' from the building.
Tank and controls will be in the crawl space, (6' high). Do I have to mount a disconnect outside "within site" of the well? Along with the disconnect that will be next to the controller at the tank? What's common? As you see I'm in Washington.
RAW
 
Re: Well Disconnect

I feel it would be best to install the means of disconnect visible and not more than 50' from whatever equipment is to require servicing and or adjustment by persons, or per Article 430.102 of the NEC. (locking provision exception) This might mean a disconnect for the controller and a separate disconnect for the well equipment. :)
 