I hope someone has an answer for this. I had a customer call with a high copper content in his water test. There are blue-green stains in his sinks. He said he never had this problem until the well pump was changed a few years ago and it has gotten progressively worse. The pump is a 110vlt. deep well, (160'). The grounding conductor FROM the pump was bonded to the steel well casing but not brought back to the panel. The service is a 100 Amp single phase 2 wire service lateral with grounding electrodes at the meter and none at the service panel about 75' away. The meter is on the utilities pole with the transformer. I amp probed the utility grounding electrode conductor and the hot conductor to the pump at the same time. When the pump comes on the utility grounding electrode conductor shows 3 amps current flow. We did this several times. This indicates a fault in the pump or wiring in the well casing to me so I ran a #6 bare copper from the well casing to the panel ( about 10 ft.) expecting the breaker to trip when the we ran the pump again. This is where I'm stumped. The utility grounding electrode conductor still showed the 3 amps but the #6 to the panel nothing and yes the main bonding jumper is in the panel. Any help would be appreciated. Thanks, Pat.