Re: Well pump
Rigid steel conduit would also protect the well pump line from lightning as well. You should also run an external grounding electrode conductor because the well casing makes for a h#!! of a ground stake. The GEC would need to be in schedule 80 pvc. Where subject to mechanical damage could be protected by pressure treated wood guard strips or 2 galvanized conduits that are 1 size larger and installed as guard strips.
You do not want to run the GEC to the well casing in steel conduit. You would have a hard time bonding it and for practical purposes all of the grounding electrode current flows over the outside of the steel conduit.
One way implement the whole shebang is to use 1' GRC for the powerline, 3/4" schedule 80 PVC right next to the GRC for the grounding electrode conductor, then install a dummy length of 1" GRC on the other side of the PVC conduit. The GEC would need to be bonded using a copper only box lug ( preferably the direct burial kind that uses a bronze setscrew ) and a stainless steel bolt threaded into the casing and capped on the other side with a stainless hex nut and an acorn nut.