I looking in the NEC 2011 book were it state what is the smallest wire that can be paralleled?
I thought I have seen this before.
I thought I have seen this before.
I looking in the NEC 2011 book were it state what is the smallest wire that can be paralleled?
I thought I have seen this before.
I looking in the NEC 2011 book were it state what is the smallest wire that can be paralleled?
I thought I have seen this before.
Smallest #20 -- see 620.12(A)(1)
Do you really think he is running an elevator traveling cable?
He didn't say. He said 'smallest'.
I know what he said but lets use our heads.:thumbsup:
We don't even have to go to article 620 to say 20 AWG, all we have to do is look at exception 1 to 310.10(H) to find there is no bottom limit to the size conductor we can parallel.
But I am going to use commonsense and say the answer to the OPs question is 1/0.
I agree that the common sense answer would be 1/0. But one could argue that without further information from the OP, the answer COULD be either no minimum, as EX 1 allows, or 20 AWG as 620 allows.
The OP's question is one that a real screwy test question could come from, as there are at least three mentions of min. size in the NEC, and they don't come close to agreeing.
What if the OP was an apprentice working on elevators and left that info out? Or was running instrumentation wiring?
To each their own.
In my view if the question was about elevator cables the OP would have mentioned it. But you learned a new code section so life is beautiful.![]()
The OP gave no circumstances. I don't know if it was a bar bet, a question on a master's exam, or what.
BTW the #20 is a good way to win a bar bet or possibly get an answer right on a master's exam.
But it is incorrect.
There is no bottom limit if we use exception 1
Maybe, maybe not.
We have to use Chapter 3 wiring methods. The smallest conductor in Table 310.13(A) is 22 AWG MTW. Thus, the smallest conductor we could use under Exc. 1 would be 22 AWG, would it not?
I will agree with that.
And just where in the OP's question does it specify that the question is limited to Chapter 3 wiring methods?Maybe, maybe not.
We have to use Chapter 3 wiring methods. The smallest conductor in Table 310.13(A) is 22 AWG MTW. Thus, the smallest conductor we could use under Exc. 1 would be 22 AWG, would it not?
So, it only took 14 posts over a day and a half to agree on an answer for the OP's question.
We may not be good, but at least we are slow.
![]()
Always glad to help uphold traditions!Heck, 14 posts is pretty good. At least it was not 14 pages.
(Never mind, I see GD has ensured we can keep going)![]()
And just where in the OP's question does it specify that the question is limited to Chapter 3 wiring methods?
Instrument and control wiring are in the NEC too. Field wiring for them, that is. And electricians can install such wiring.