In a ground floor interior conference room with metal conduit stubbed above the ceiling (non-plenum), in the slab to a floor box under the table there is an electrical and data outlet. The inspector stated that the data cable needs to be outdoor rated. He then issued a notice for re-inspection stating that "110.3(B) or 800.113 must show me that your cable is listed for wet and damp location. UTP type cable is listed for wet damp location."
110.3(B) and 800.113 just state that the cable must be listed and labeled for proper use.
NEC 100 Definitions I. General defines - Location, Wet. Installations underground or in concrete slabs or masonry in direct contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas; and in unprotected locations exposed to weather. - So he's got me on concrete slab in direct contact with the earth
but
800.47 states The requirements of 310.10(C) shall not apply to communications wires and cables.
I would just replace the CMR rated cable pulled with CMX rated but I feel like that would be a violation as well as the total run is about 125' from IDF to floor box and the conduit is only under the floor and up the wall (30').
Should I just run the CMX rated cable in the conduit and then switch it to the CMR above the ceiling for the 95' run back to the IDF since CMX can't be run in vertical runs or riser communication raceways or riser cable routing assemblies as per 800.154(a) or plead my case with a different argument?
110.3(B) and 800.113 just state that the cable must be listed and labeled for proper use.
NEC 100 Definitions I. General defines - Location, Wet. Installations underground or in concrete slabs or masonry in direct contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas; and in unprotected locations exposed to weather. - So he's got me on concrete slab in direct contact with the earth
but
800.47 states The requirements of 310.10(C) shall not apply to communications wires and cables.
I would just replace the CMR rated cable pulled with CMX rated but I feel like that would be a violation as well as the total run is about 125' from IDF to floor box and the conduit is only under the floor and up the wall (30').
Should I just run the CMX rated cable in the conduit and then switch it to the CMR above the ceiling for the 95' run back to the IDF since CMX can't be run in vertical runs or riser communication raceways or riser cable routing assemblies as per 800.154(a) or plead my case with a different argument?