rszimm
- Tucson, AZ
Running conduit outdoors has always been a bit of a mystery to me as to which fittings are required. So let's limit this to a typical outdoor setting where the conduit is likely to come in contact with rain (e.g. not underground or in a car wash or anything like that). So, 312.2 states "For enclosures in wet locations, raceways or cables entering above the level of uninsulated live parts shall use fittings listed for wet locations", implying that if you're entering below those parts, you don't need wet location fittings. However 314.15 states "Boxes, conduit bodies, outlet box hoods, and fittings installed in wet locations shall be listed for use in wet locations". So, if i use the standard knockouts at the lower half of a breaker box/meter box/disconnect/etc, do I need to use wet fittings or not? 314.15 seems to say "yes". 312.2 seems to say "no".
Second question. In this same "wet" environment are threaded rigid connections sufficiently waterproof? I.e. if I had two threaded conduit bodies a few inches from one another and ran a threaded rigid nipple between them, wrench tight, no lock-nuts, is that OK? Do I need to put pipe-dope on them to seal? Maybe a sealing lock-nut?
Final question. When running into a breaker box with a rigid nipple, my understand is I need a regular locknut on the outside and a bonded one on the inside whenever I use a factory knockout toward the bottom of the enclosure, but I need a sealing locknut on the outside and a regular locknut on the inside if I drill a hole toward the top of the box. Correct?
Again, always been confused by this in the past and usually just throw a bunch of sealing locknuts all over the place and always use "wet location" fittings