I am in design on a small (16' internal diameter) telescope observatory dome. There will be control cabling (USB, RS232 serial, etc.) from the telescope in the center of the dome to a PC workstation on the inside perimeter of the dome. The client is looking for a system to avoid the control cabling being run loose on the ground from the telescope to the workstation to reduce the tripping hazard. The client proposed solution is to provide trench ducts with removable covers from the telescope to the workstation.
The floor is going to be a 5" thick concrete slab sitting on top of 6" of gravel backfill. Wouldn't this make the trenches wet locations per Article 100 (2017) "Installations underground or in concrete slabs or masonry in direct contact with the earth" and subsequently require the conductors inside the raceway to be wet location listed? The control cabling that comes with the telescope is not wet location listed and I doubt any future control cabling the client would provide would be wet location listed, so I am reticent to support the trench concept. The dome will not have HVAC (don't ask me why), so I am concerned about the potential for moisture buildup in the rest of the space.
Our initial proposal was to use overfloor raceway (https://www.legrand.us/wiremold/rac...oor-raceway/ofr-series-overfloor-raceway.aspx), but the client shot that down over concerns about that equipment holding up in a non-conditioned space.
The floor is going to be a 5" thick concrete slab sitting on top of 6" of gravel backfill. Wouldn't this make the trenches wet locations per Article 100 (2017) "Installations underground or in concrete slabs or masonry in direct contact with the earth" and subsequently require the conductors inside the raceway to be wet location listed? The control cabling that comes with the telescope is not wet location listed and I doubt any future control cabling the client would provide would be wet location listed, so I am reticent to support the trench concept. The dome will not have HVAC (don't ask me why), so I am concerned about the potential for moisture buildup in the rest of the space.
Our initial proposal was to use overfloor raceway (https://www.legrand.us/wiremold/rac...oor-raceway/ofr-series-overfloor-raceway.aspx), but the client shot that down over concerns about that equipment holding up in a non-conditioned space.