Thanks for the replies. It looks like I should expand on the situation. This is a job we are performing at a university research facility. There are approximately 60 runs of conduit crossing the concrete ceiling. There is also a crane rail system (by others, not in our scope) with exposed 480v copper buss bars. We are in a dispute with the CM over whether the note, "all devices in wash down areas shall be provided with waterproof in-use covers", makes the entire room a wet location thus requiring rigid conduit and stainless boxes on the ceiling per their spec. This is the only information given on the drawings or in the specs pertaining to this room being a wet location. We did consider everything going down the walls a wet location in our take off and installed accordingly. We considered the ceiling a dry location and installed accordingly. Our thinking was that the devices called out in the note are all located below 48" in height. We thought it would be unusual for water to spray from a wash down area over 30ft high onto the ceiling. We also questioned the wisdom of an exposed 480v copper buss in such an area. They have accepted the EMT conduit but want stainless boxes. They also want a credit for the rigid conduit work not performed.
I think we're going to lose this one but I'd like some other input. Thanks!
Keith