Our specifications for our nurse call systems require conductors to be rated for wet locations if it is installed below slab on grade in PVC conduit which than changes into EMT in a pipe chase going vertical for several floors. The only time it is free aired is in the electronics room.
The contractor has stated where the conduit comes up in the pipe chase it is considered a riser so the any wire that has a water inhibitor cannot be brought up in the conduit without switching over to a riser rated cable. The system is 24 volt. Would conductors / cables in a conduit / pipe chase be required to be rated for riser applications Per NEC? We suggested PLTC rated for wet locations.
The contractor has stated where the conduit comes up in the pipe chase it is considered a riser so the any wire that has a water inhibitor cannot be brought up in the conduit without switching over to a riser rated cable. The system is 24 volt. Would conductors / cables in a conduit / pipe chase be required to be rated for riser applications Per NEC? We suggested PLTC rated for wet locations.