J jbolen Senior Member Apr 22, 2020 #1 I have Belden cable rated for indoors, outdoors and sunlight resistance. Would this cable be rated for underground wet locations ?
I have Belden cable rated for indoors, outdoors and sunlight resistance. Would this cable be rated for underground wet locations ?
petersonra Senior Member Location Northern illinois Occupation engineer Apr 22, 2020 #2 jbolen said: I have Belden cable rated for indoors, outdoors and sunlight resistance. Would this cable be rated for underground wet locations ? Click to expand... Does it claim to be?
jbolen said: I have Belden cable rated for indoors, outdoors and sunlight resistance. Would this cable be rated for underground wet locations ? Click to expand... Does it claim to be?
electrofelon Senior Member Location Cherry Valley NY, Seattle, WA Apr 22, 2020 #3 jbolen said: I have Belden cable rated for indoors, outdoors and sunlight resistance. Would this cable be rated for underground wet locations ? Click to expand... IMO if it is "wet locations" than underground in a raceway is ok, but no direct bury. It would need to be marked direct bury.
jbolen said: I have Belden cable rated for indoors, outdoors and sunlight resistance. Would this cable be rated for underground wet locations ? Click to expand... IMO if it is "wet locations" than underground in a raceway is ok, but no direct bury. It would need to be marked direct bury.
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Apr 22, 2020 #4 I agree. Inside a raceway you are fine but not db.