I am having a rather deep dive discussion with a non-electrical engineer regarding NEC wet locations:
"where exposed to weather" is one of the specific definitions I recall in defining a wet location.
In our discussion, I pointed out that an aerial installation (on a messenger or not) would be or could be defined as a wet location.
Further on in the conversation, it was asked if a TC-ER cable listed for aerial installation, though not specifically indicated for use in a wet location is contradictory, since by the listing as tray rated, exposed or extended run or in an aerial install, the cable would or could be exposed to weather. Since the cable maybe listed for use in direct sunlight, is moisture resistant and chemically resistant and listed for aerial installation, how does one determine the suitability of wet vs. dry locations? Where is the line?
What if the manufacturer states, dry locations, and also states aerial installation, and suitable for all approved raceways, no direct burial?
I reviewed Article 336.10(c) and ticked positive or compliant for all of the applicable aspects for 336.10 (1) through (7) a. through g, (8), (9), the exceptions and (10) - based on our hypothetical cable type (UL listed TC-ER, dry locations, 90C, Fire resistant - 2hrs @2000F + other flame test, sunlight, moisture, chemically resistant, installed in cable tray & RMC, no direct burial or aerial aspects of the installation, industrial area serviced by qualified personnel only, no public access - highly controlled site, cable not exposed to physical damage and fully supported every 6ft.)
Thoughts, comments? Is my point all wet? (no pun intended.)
"where exposed to weather" is one of the specific definitions I recall in defining a wet location.
In our discussion, I pointed out that an aerial installation (on a messenger or not) would be or could be defined as a wet location.
Further on in the conversation, it was asked if a TC-ER cable listed for aerial installation, though not specifically indicated for use in a wet location is contradictory, since by the listing as tray rated, exposed or extended run or in an aerial install, the cable would or could be exposed to weather. Since the cable maybe listed for use in direct sunlight, is moisture resistant and chemically resistant and listed for aerial installation, how does one determine the suitability of wet vs. dry locations? Where is the line?
What if the manufacturer states, dry locations, and also states aerial installation, and suitable for all approved raceways, no direct burial?
I reviewed Article 336.10(c) and ticked positive or compliant for all of the applicable aspects for 336.10 (1) through (7) a. through g, (8), (9), the exceptions and (10) - based on our hypothetical cable type (UL listed TC-ER, dry locations, 90C, Fire resistant - 2hrs @2000F + other flame test, sunlight, moisture, chemically resistant, installed in cable tray & RMC, no direct burial or aerial aspects of the installation, industrial area serviced by qualified personnel only, no public access - highly controlled site, cable not exposed to physical damage and fully supported every 6ft.)
Thoughts, comments? Is my point all wet? (no pun intended.)