Golfnut1
Member
- Location
- los alamos, new mexico
I was just wandering, in the 2011 NEC ,Article 300.5b states that the interior of any raceway or enclosure installed underground shall be considered as wet locations and the conductors installed in these raceways or enclosures shall be listed for use in wet locations. Then in Article 300.9 it states that where raceways are installed in wet locations above grade, the interior of these raceways shall be considered to be a wet location. My question is, if the interior of a raceway is considered a wet location underground and above ground in wet locations and the conductors installed in these raceways shall be listed for use in wet locations, then why isn't the interior of an enclosure above ground in wet locations considered a wet location and the conductors installed in these enclosures be made to be listed for wet locations. If it is in the code somewhere, I cannot find it.