I have been questioned by a friend on grounding an under water luminaire. He asked me to find the article for sizing the egc for the under water lum. He states that he ran an 8 awg to the lug on the mounting enclosure. He did not run another ground to the cord connected lamp housing inside that mounting enclosure because it already has an egc inside the cable. There is a lug outside of the lamp housing that he did not run an egc to.
The inspector wants him to run an insulated 8 awg to that lamp enclosure. There is already an 8 awg to the housing in the pool wall and a 12 awg to the lamp enclosure.
Under 680.23 (B)(3) and (F)(2) I told him that a insulated 12 awg should be sufficient (per code)since the current carrying conductors are 12 awg. Aside from the AHJ having the upper hand, there is no room in the conduit to run an insulated 8 awg.
Am I giving the correct information or am I missing something?
The inspector wants him to run an insulated 8 awg to that lamp enclosure. There is already an 8 awg to the housing in the pool wall and a 12 awg to the lamp enclosure.
Under 680.23 (B)(3) and (F)(2) I told him that a insulated 12 awg should be sufficient (per code)since the current carrying conductors are 12 awg. Aside from the AHJ having the upper hand, there is no room in the conduit to run an insulated 8 awg.
Am I giving the correct information or am I missing something?