jumper

Senior Member
Maybe. Depends of what type of insulation the cable has.

Examples:

UF-yes

THWN-yes

USE-no

USE/RHW-yes

URD-no.

What cable are you using and where?

And why is this question in hazardous locations? Need more info/details to answer correctly.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Looking at it another way, the fact that it is wet rated does not by itself prevent it from being used in a dry area outdoors. But there are separate properties, like flame spread, that may prevent it from being used indoors, whether the indoor area is wet or dry. :)
 