I have sewage pump wet-well classified by an engineer as Class 1 Div 1
I have 2" PVC Conduit encased in concrete 24" deep with terminal ends flush with the interior of the wet well.
The PVC transitions to PVC Coated aluminum conduit and terminates in a 36 x 36 non-explosion-proof box with terminal strips.
The j box has other entries to a control cabinet with seal-offs in that run.
The design is supposed to eliminate the need for a seal off of the pump cables.
It seems to me the 2" conduits (from the wet well) would need a boundary seal before entering the j box.
Even if the j box is explosin proof the fact that the conduits are 2" would require seals per 501.15(A)(2)
Input desired !!!