Service call. Customer tells me that 20 amp breaker keeps trippin.
He had another electritian look at it. guy spent two hours found 2 or three amps in circuit, puzzled he left. told HO sorry i don;t know what is causing this.
It was acting like a short, but only after some time being on. At first i thought it was an overlod.
After asking all my questions and 2 hours i found the problem.
Roof had been leaking, dripping inside outside wall, where there is a recep. Apparently getting all the wires going to it wet.
took receptacle out, disconnected cables (HO decision), problem solved.
-What kind of damage do you think water did to the romex?
-Did it create a short within the cable?
-Would the water eventually act like a conductor between them?
Keep in mind that the breaker would trip after 2 or 3 min.But before we got some rain it would trip after a couple of hours.
Breaker is not AFCI or GFCI.
He had another electritian look at it. guy spent two hours found 2 or three amps in circuit, puzzled he left. told HO sorry i don;t know what is causing this.
It was acting like a short, but only after some time being on. At first i thought it was an overlod.
After asking all my questions and 2 hours i found the problem.
Roof had been leaking, dripping inside outside wall, where there is a recep. Apparently getting all the wires going to it wet.
took receptacle out, disconnected cables (HO decision), problem solved.
-What kind of damage do you think water did to the romex?
-Did it create a short within the cable?
-Would the water eventually act like a conductor between them?
Keep in mind that the breaker would trip after 2 or 3 min.But before we got some rain it would trip after a couple of hours.
Breaker is not AFCI or GFCI.