No, that's just a terminal box, where the service conductors connect to the horizontal bus-bars.And some type of CT enclosure on left.
I know WA had an exception for the serviceThat’s what I saw. Expensive mistake.
And some type of CT enclosure on left.
If POCO does not allow then it’s really expensive
But cant you only have a Max of six grouped in one location?Funny, there are only 6 disconnects being used. Even with 7 we would have to know what they are serving 230.2(A) & 230.72(B) to actually know if there's a problem.
Yes six is the maximum per service unless additional disconnects meet the exception like for a fire pump. You could have 10 services with 60 disconnects in one location.But cant you only have a Max of six grouped in one location?
Depends on 230.2 and 230.72. In the picture the unused disconnect could be removed and blanked.But cant you only have a Max of six grouped in one location?
There can be multiple disconnects, 230.71I would think the service disconnect have to be in there own enclosure. Even if they had only had six. Question, is there an exception for meter packs.
but 230.72(B) says:Yes six is the maximum per service unless additional disconnects meet the exception like for a fire pump. You could have 10 services with 60 disconnects in one location.
see post #8, WA is not enforcing that until more compliant equipment becomes available.I would think the service disconnect have to be in there own enclosure. Even if they had only had six. Question, is there an exception for meter packs.
So that means there is not yet any violation in the photo?Funny, there are only 6 disconnects being used.
That's the way I see itSo that means there is not yet any violation in the photo?
Cheers, Wayne
If Poco seals service wire side, & prohibits taps from there, then are customer side meter-pack taps a listing violation?If POCO does not allow then it’s really expensive