Folks, I've been doing a redesign of an emergency circuit in a building and when I was doing the new panelboard schedules I saw that the original design (less than 3 years old) had on its panelboard schedules figures that do not match what I've always used....
All voltages are 120/208
example1: panelboard X
TOTAL VA (ALL LOADS) = 137,368 VA
TOTAL AMPS (calculated by me) = 137368/208/1.732 = 381.3A
TOTAL AMPS (shown on original design drawings) = 423(!)
example2: panelboard y (same building, same design)
TOTAL VA = 173,261VA
TOTAL AMPS (MY CALCULATION) = 173261/208/1.732 =480.9A
TOTAL AMPS SHOWN ON ORIGINAL SCHEDULE (with above data) = 502
the difference is not even, lets say the same k factor... the design has several panels and none of them do match my calculation.. it is also interesting that the max phase amps matches the existing design (when I use 120v and single phase calculation with the most loaded phase)
please, can anyone show me what am I missing if anything...
thanks a lot.
All voltages are 120/208
example1: panelboard X
TOTAL VA (ALL LOADS) = 137,368 VA
TOTAL AMPS (calculated by me) = 137368/208/1.732 = 381.3A
TOTAL AMPS (shown on original design drawings) = 423(!)
example2: panelboard y (same building, same design)
TOTAL VA = 173,261VA
TOTAL AMPS (MY CALCULATION) = 173261/208/1.732 =480.9A
TOTAL AMPS SHOWN ON ORIGINAL SCHEDULE (with above data) = 502
the difference is not even, lets say the same k factor... the design has several panels and none of them do match my calculation.. it is also interesting that the max phase amps matches the existing design (when I use 120v and single phase calculation with the most loaded phase)
please, can anyone show me what am I missing if anything...
thanks a lot.