Senior Member
- Location
- Raeford, NC
Here is the scenario I am involved with. I am doing the gen. wiring on a building for a ball field. An out of state contractor is doing the lighting for the ball fields. Here is their set up. 480v 3 phase Panel with 600 amp main breaker. In this panel there are 14 30amp 3 pole breakers, on the top of the buss there are feed thru lugs which feeds another 600amp rated main lug panel with 11 30amp 3 pole breakers. Here is where it is a head scratcher. The contractor has pulled 3 500mcm's to the poco pad mount transformer 320' away. By 310.16 500mcm in the 75deg. coll. rates it for 380amps.
I do not know the draw for the lighting but the 24 30 amp breakers feed 24 poles with 5 lights each. and one breaker feeds a 480/208-120 30 kw transformer.
I know it's not my install but what am I missing with the sizing of the service conductors?
I do not know the draw for the lighting but the 24 30 amp breakers feed 24 poles with 5 lights each. and one breaker feeds a 480/208-120 30 kw transformer.
I know it's not my install but what am I missing with the sizing of the service conductors?